A/C question

Page 2 of 4  

you dont change it after each use, or its just been sitting or what?

i would recommend johnstones, although they may require you have an account with them.
--
Nathan W. Collier
http://InlineDiesel.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

change.
This is an industrial vacuum pump and nowhere does it say to change the oil after each use. Probably because it was not built for the sole purpose of air conditioning service. Actually, it used to live at Bendix with about 5 of its brothers running 24/7 to test flight control systems.

account
Ok, I will check that out.
--
If at first you don't succeed, you're not cut out for skydiving



Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

if they tell you that you need an account, use mine.
--
Nathan W. Collier
http://InlineDiesel.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
On 8/17/05 6:34 PM, in article snipped-for-privacy@corp.supernews.com, "Nathan

You mean your bank account :))), I could use some Dale
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
I just did a compressor change out on an 1989 F-250. I used a commercial vacuum pump that pulled a vacuum of around 27. What I want to comment on is that my FORD service manual states pull a vacuum of at least 25 for a max of 30 minutes if the whole system had been replaced. Now 25 is not that great of vacuum and far less than someone on this group has been saying is required. So far I did everything that the FORD manual stated and everything seems to be working OK. What I also found interesting is that the FORD manual said after you disconnect the vacuum pump make sure that the system will hold that vacuum for at least 5 minutes. Now I do have a problem with this statement. I would probably be bringing the new compressor back for a refund it is only held a vacuum for 5 minutes.
Ron
TBone wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

you pulled 25Hg. thats not the same thing as 500 microns.

youre reading it wrong. it means to wait at least 5 minutes to make sure it holds the vacuum. if it will hold vacuum for 5 minutes it will hold vacuum indefinately.
--
Nathan W. Collier
http://InlineDiesel.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
It states (the FORD service manual) at least 25 inches of Mercury and as close to 30 that you came get. You are right that is not the same as 500 microns. So how does microns relate to inches of mercury ?
So what is so magical about 5 minutes why not 2 minutes or 10 minutes or 24 hours ? I help a vacuum over night on the last job with no problem but the compressor seals would not work in reverse so the vacuum test was basically worthless as far as telling me the seals were good ?
Nathan W. Collier wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Pulling a vacuum helps in the determination of whether a system is leaking or not. More importantly you do it to remove non-condensibles from the system.

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Micron is really almost a useless measurement to almost anyone that is reading this newsgroup. It cannot be measured with the equipment available to the service or home repair person. Vacuum pumps are specified in volume/sec and inches of mercury. Volume is not important to us because we are working in a closed system if we had a hole in one end and were trying to keep a vacuum inside then volume per minutes would be very important now I sure hope everyone knows that you must have your AC system closed before you start drawing your vacuum. So now all we need to do is determine what the min vacuum we need to pull and from what I understand now about this subject almost anything that will draw a vacuum will work just fine on our AC systems if it can acheive a certain ?? inches of Mercury. So now lets get off this micron issue and on to something that we all can measure. If a manufacture of a specific vacuum pump states it can draw 50 micron then at what inches of mercury are they talking because then any vacuum pump that can achieve that pull will do that same thing, volume again is not important.
Thank you, Ron in Phx, AZ where AC is required.
Ron wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

.....if you dont care about doing the job properly that is.

?? i paid less for my micron gauge than i paid for my pressure gauges.

if it can pull 500 microns it will work just fine in your a/c systems. if it wont (and it wont) its _not_ "ok" to use it. sure it will make the system run and cool but it will NOT cool as efficiently as it would if it were done right. the suggestion that it will is irresponsible at best.
--
Nathan W. Collier
http://InlineDiesel.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

No, any self respecting residential service tech has a micron gauge. I don't have a clue how often they're used in automotive AC but I suspect not often.

A micron is 0.001mm. There are about 25400 microns to an inch. A gauge set simply doesn't have the resolution to measure a 500 micron vacuum.
BTW, a perfect vacuum would be 0 microns. 500 microns is 0.5mm.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

Micrometers... 1 millionth of an inch. 1" of Hg = 25,400 microns of Hg. However, the scale is inverted. In other words, a perfect vacuum (29.921" of Hg at sea level) is 0 microns. Therefore, 500 microns is about 29.903" of Hg.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

microns are smaller incriments of measure and are much more "sensitive" and accurate than Hg.

its just a guestimate. i typically do something else for 15 minutes and check back.

if thats the case you should charge the system with nitrogen and make sure it maintains pressure.
--
Nathan W. Collier
http://InlineDiesel.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
will someone please answer the question that was asked a couple posts ago:
what does '500 microns' equal in inches of mercury ?

and
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

I thought I did... 29.903"
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

You did, he wasn't paying attention in class. Gary, go stand in the corner.<G>
Roy
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Tom Lawrence wrote:

OK got that one answered now I would like to see a temperature chart of the center register discharge temperature versus vacuum drawn on your typical fixed orifice tube auto AC system.
From No vacuum pulled in five degree steps to 29.903 which is almost a perfect vacuum.
I personally believe that what you will see is a straight line or two straight lines with anything between these two temps being OK and that vacuum is not related to the temperature output on your typical auto AC at all. The size and condition of the system, the fixed orifice tube and the amount of oil in the system will set the output temp.
Please prove me wrong on this because if a super vacuum will get my AC 20 degrees cooler here in Phx, AZ I am for it.
I did see yesterday that there is a new fixed orifice tube that is really not fixed but variable that is claiming 12 degree better cooling at idle of course I found this after I filled the system with a new charge. If I had a recovery tank I would be installing one of these.
The purpose of drawing a vacuum is to get the moisture out of a system that will cause corrosion and I real believe that is all. Right or Wrong ? I need hard facts or a website that explains this in detail if a vacuum will really drastically improve cooling.
Thanks Ron
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

if you have moisure or non-condensables in your system it cannot possibly work as efficiently as it would if it were pulled down into a proper vacuum.

nobody said 20 degrees. if you pull a vacuum with a pressure gauge and a refrigerator compressor you might see a difference of 8-10 degrees. if you use a better vacuum source the difference may only be 1-2 degrees...but there will be a difference. we within the industry dont spend $300 for a decent 2 stage vacuum pump for the hell of it. we do it because as professionals we want to give you the best service possible and that means doing it right. if the cheaper alternatives were "ok" we would certainly use them (i got dozens of compressors of all types and size that it ok off jobsites in equipment being replaced) and same some money.

and non-condensables which hinder cooling and can be fatal to compressors and metering devices.
--
Nathan W. Collier
http://InlineDiesel.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload
Now that sounds a lot better 1 to 2 degrees is not worth my money as a home repair do it yourself person unless I can find a good suction pump used really cheap. When it 120 ambient and the inside of the car is in the 160 degree range 1 to 2 degrees will not be detected. 10 to 12 maybe but questionable. I have no problem with a professional using the best possible tools if they understand them and aren't just using them for show. I am afraid most do not understand them though and might not even use them most of the time.
I turned my AC on this morning. I installed a new compressor yesterday. The air was so much colder I turned the fan down to low and all of a sudden got smoke that smelled like wood burning coming out of the vents. I thought about it for a while then determined there must be something in the resistors that control the fan that got burned. Sure enough it was packed with leaves. I did get a good look at the evaporator and could see that it was really packed with stuff also so off with the sides to see if I could wash it out. Got the garden hose with a high pressure nosel on it and now it looks like it will pass some air. I have no doubt that it was almost 50 per cent restricted. Just about ready to reassemble and see now much better it will be.
So how do all these other non-condensables get into a closed system ? Moisture I understand and metal parts for things breaking but if the system came from the factory with a good charge and then a seal started to leak I would not expect to have anymore non-condensables in the system after I replace the compressor than before I replaced it other than mybe some moisture from having the system opened.
Back to work (I guess a retired person shouldn't use the word work so back to my fun project)
Ron
Nathan W. Collier wrote:

Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload

bear in mind that its also an issue of compressor/metering device damage. it may only shorten component life by a little, but it will shorten component life.

its no longer a closed system once you open it to replace the compressor or other components. you also have component disentigration, minute particles left from machining the new components, etc. where you have moving parts, you have wear.
--
Nathan W. Collier
http://InlineDiesel.com
  Click to see the full signature.
Add pictures here
<% if( /^image/.test(type) ){ %>
<% } %>
<%-name%>
Add image file
Upload